I am getting conflicting information concerning transformer requirements for a SkyBell HD in the UK.

The SkyBell web site shows the following for set up with a chime:
http://www.skybell.com/content/uploads/2016/08/SB_doorbell_both.pdf
It indicates that you need a 10-36V AC transformer. When I contacted SkyBell in the US they advised that I could use the built in transformer on a Byron 776 chime ie no additional transformer required. However, when I contacted the EU distributor for SkyBell I was advised that
"the built-in transformer (The Byron 776 chime) does not work with the skybell because the skybell needs 12 volts to work properly. and the Byron 776 is an 8 volt transformer."

"Skybell HD requires permanent power 12vdc - 19vdc 2A  Due to the difference in frequency (USA 60Hz - Europe 50HZ) we do not support the usage of an AC transformer.

You will find the right power adapter in our webshop
Skybell Poweradapter  12 Volt DC EU

The Byron 776 chime is a gong that you can use only the transformer not.”

Has anyone installed the SkyBell HD in the UK and any advise re. an appropriate chime and transformer? Can the SkyBell work off AC or DC current of the appropriate voltage?

Thanks

Tony
Reply

Use magic Report

11610K

Threads

12810K

Posts

37310K

Credits

Administrators

Rank: 9Rank: 9Rank: 9

Credits
3732793
1-12-2019 21:44:51 Mobile | Show all posts
Apologies for jumping on an old thread, but I'd like to know if you resolved this. The SkyBell FAQ explicitly says


What are the power and voltage details?

Voltage 120/1130v AC, or 220/230/240v AC Transformer Range: 8-36v AC, 8-15 VA Low Voltage Transformer(UK/Europe) 8-36v AC, 1 AMP 8-15 VA.​
but it's not 100% clear whether that's only for the original version or includes the HD version.
Reply Support Not support

Use magic Report

1-12-2019 21:44:52 Mobile | Show all posts
I’ve had/have the following SkyBells installed (all bought from US directly) and never had to install any transformers - they simply replaced my mains wired regular doorbell (220-240v)
SkyBell original
SkyBell HD
Skybell HD trim (current)
Reply Support Not support