The 3600TL could well yield more annually than a 4000TL.
For all the times when you're not peaking close to 4kWh then the 3600TL will probably be more efficient.
Get your company of choice to run figures for both inverters with your chosen panels through their software of choice, PVSOL being a popular one and see what it says.
I have a 4kWp system with a Fronius IGTL3600 inverter. I personally chose this over 4000TL inverters because it yielded more in my case.
This text is taken for THIS ARTICLE
"It is common in the industry to oversize the PV array by using a PVto- inverter sizing ratio of around 1.15. After all, a well-designed system will typically have end-to-end system losses of about 15%–16%. Oversizing the array ensures that the inverter is driven to its maximum output, at least during the best sun hours of the day. System designers who are looking at a 20-year design life for the system will usually size the array-to-inverter using a 1.2 to 1.25 ratio. Some PV system integrators even routinely use a 1.3 ratio." |
|