Without knowing if you have 2 different heating zones (one for radiators, one for UFH) on the heatpump or a single heat zone feeding both then it's hard to say. Where is your Nibe installer and what have they done to get the system going?
My Nibe unit only has a single heating zone feeding my system (underfloor heating throughout) and I run my heating circuit at a fixed target temperature of 38 degrees when a manifold needs heat and 10 degrees when no heat is needed (i.e. the heating circuit shuts down).
One thing to watch out for is that your immersion heaters are not switching in unnecessarily. They will operate if you are asking for too high a flow temperature for your rads - hopefully your plumber has significantly oversized your rads so they work at a much lower flow temperature. |
|